How can resolve problem F01011 fault in siemens 6RA80 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Download interrupted. The project download was interrupted.

Fault value (r0949, decimal interpretation):
1: The user prematurely interrupted the project download.
2: The communication cable was interrupted (e.g. cable breakage, cable withdrawn).
3: The project download was prematurely ended by the commissioning software (e.g. STARTER, SCOUT).
100: Different versions between the firmware version and project files "Download from card".

Remedy:

- check the communication cable.
- download the project again.
- boot from previously saved files (power-down/power-up or p0976).
- when downloading from the card, use the matching version.