How can resolve problem F01039 fault in siemens 6RA80 DC Drive ?
1 Reply
Jun 13, 2022 4:53 pm
Cause : ACX: Writing to the parameter back-up file was unsuccessful. Writing to at least one parameter back-up file PSxxxyyy. in the non-volatile memory was unsuccessful.
Remedy:
- check the file attribute of the files (PSxxxyyy., CAxxxyyy., CCxxxyyy.) and, if required, change from "read only" to "writeable".
- check the free memory space in the non-volatile memory. Approx. 80 kbyte of free memory space is required for every drive object in the system.
- replace the memory card or Control Unit.