F01122 fault in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Reactions
182 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F01122 fault in siemens 6RA80 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Frequency at the measuring probe input too high. The frequency of the pulses at the measuring probe input is too high.

Fault value (r0949, decimal interpretation):
1: DI/DO 9 (X122.8)
2: DI/DO 10 (X122.10)
4: DI/DO 11 (X122.11)
8: DI/DO 13 (X132.8)
16: DI/DO 14 (X132.10)
32: DI/DO 15 (X132.11)
64: DI/DO 8 (X122.7)
128: DI/DO 12 (X132.7)

Remedy: Reduce the frequency of the pulses at the measuring probe input.