F01151 fault in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Reactions
175 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F01151 fault in siemens 6RA80 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause :CU: Number of drive objects of a category exceeded. The maximum permissible number of drive objects of a category was exceeded.

Fault value (r0949, interpret hexadecimal):
ddccbbaa hex:
aa: drive object category.
bb: Max. permissible number for this drive object category.
cc: Actual number for this drive object category.
dd: No significance.

Remedy:

- power down the unit.
- suitably restrict the number of drive objects of the specified category by reducing the number of inserted components.
- re-commission the unit.

Reply