How can resolve problem F01200 fault in siemens 6RA80 DC Drive ?
1 Reply
Jun 14, 2022 1:41 am
Cause : CU: Time slice management internal software error. A time slice management error has occurred.
It is possible that the sampling times have been inadmissibly set. Fault value (r0949, interpret hexadecimal):
998: Too many time slices occupied by OA (e.g. DCC)
999: Too many time slices occupied by the basic system
Too many different sampling times may have been set.
Remedy: - check the sampling time setting (p0112, p0115, p4099).