How can resolve problem F01303 fault in siemens 6RA80 DC Drive ?
1 Reply
Jun 14, 2022 2:14 am
Cause : DRIVE-CLiQ component does not support the required function. A function requested by the Control Unit is not supported by a DRIVE-CLiQ component.
Remedy:
Upgrade the firmware of the DRIVE-CLiQ component involved.
For fault value = 205:
Check parameter p0600 and p0601 and if required, adapt interpretation.
For fault value = 207:
Replace the power unit or if required set the device supply voltage higher (p0210).
For fault value = 208:
Check parameter p0430.23 and reset if necessary.