Forum

Share:
Notifications
Clear all

F01356 fault in siemens 6RA80 DC Drive

2 Posts
1 Users
0 Reactions
1,208 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F01356 fault in siemens 6RA80 DC Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Topology: Defective components in actual topology. The actual topology indicates at least one defective DRIVE-CLiQ component.

Fault value (r0949, interpret hexadecimal):
zzyyxx hex:

zz = connection number of component before the defective component

yy = component number of component before the defective component

xx = fault cause

xx = 1: Component at this Control Unit not permissible.

Note: Pulse enable is withdrawn and prevented.

Remedy: Remove the defective components and restart the system.

Reply
Share: