F07086 fault in siemens 6RA80 DC Drive indicate that the Parameter limit violation due to reference value change. This means a reference parameter was changed in the system. This resulted in the fact that for the parameters involved, the selected value was not able to be written in the per unit notation.
  • Check the adapted parameter value and if required correct.