F07512 fault in siemens 6RA80 DC Drive indicate that the Encoder data set changeover cannot be parameterized. This means a changeover of the encoder data set is prepared that is illegal.
- Every encoder data set must be assigned its own dedicated DRIVE-CLiQ socket.
- The component numbers of the encoder interfaces (p0141) must have different values within a drive object.