F08501 fault in siemens 6RA80 DC Drive

1 Posts
1 Users
0 Reactions
79 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

F08501 fault in siemens 6RA80 DC Drive indicate Setpoint timeout. This means the reception of setpoints from the COMM BOARD has been interrupted.

- bus connection interrupted.
- controller switched off.
- controller set into the STOP state.
- COMM BOARD defective.

  • Restore the bus connection and set the controller to RUN.
  • Check the set monitoring time if the error persists (p2040).