Siemens 6RA80 DC Drive
566
Sep 23, 2024 7:09 am
Cause : Ground fault comes when the power unit has detected a ground fault. This can happen when a live conductor comes into contact with a grounded object, such as a metal enclosure or the earth.
F30021 fault in siemens 6RA80 DC Drive indicate Ground fault. This means an electrical current flows to ground instead of following its intended path through a circuit.
- Check the power cable connections.
- Check the motor.
- Check the CT.
- Check the cables and contacts of the brake connection (a wire is possibly broken).
- Check the braking resistor.