Siemens 6RA80 DC Drive
1
Posts
1
Users
0
Reactions
97
Views
Sep 23, 2024 7:12 am
Cause : Monitoring U_ce comes when the monitoring of the collector-emitter voltage (U_ce) of the semiconductor has responded.
F30022 fault in siemens 6RA80 DC Drive indicate Monitoring U_ce condition. This means there is an hardware issue in drive power card.
Possible causes:
- Fiber-optic cable interrupted.
- Power supply of the IGBT gating module missing.
- Short-circuit at the power unit output.
- Defective semiconductor in the power unit.
Remedy:
- Check the fiber-optic cable and if required, replace.
- Check the power supply of the IGBT gating module (24 V).
- Check the power cable connections.
- Select the defective semiconductor and replace.