F30046 fault in siemens 6RA80 DC Drive

1 Posts
1 Users
0 Reactions
71 Views
Posts: 18137
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Undervoltage fault comes when a problem occurred at the power unit power supply. The voltage monitor in the internal FPGA of the PSA signals an undervoltage fault on the module.

F30046 fault in siemens 6RA80 DC Drive indicate Undervoltage fault. This means the input voltage from the power supply is below the minimum required level.

  1. Check the 24 V DC voltage supply to power unit.
  2. Carry out a POWER ON (power off/on) for the component.
  3. Replace the module if necessary.