F30080 fault in siemens 6RA80 DC Drive indicate that the current increasing too quickly. This means the power unit has detected an excessive rate of rise in the overvoltage range.
- Check the motor data - if required, carry out commissioning.
- Check the motor circuit configuration (star-delta)
- U/f operation: Increase up ramp.
- U/f operation: Check assignment of rated currents of motor and power unit.
- Check the line supply quality.
- Check the power cable connections.
- Check the power cables for short-circuit or ground fault.
- Check the length of the power cables.
- Replace power unit.