N01507 alarm in siemens 6RA80 DC Drive indicate that the Interconnections to inactive objects present. This means there are BICO interconnections to an inactive/inoperable drive object.
- Set all open BICO interconnections centrally to the factory setting with p9495 = 2.
- Make the non-operational drive object active/operational again (re-insert or activate components).