The parameter settings for an ABB ACS150 drive can vary depending on your specific application and requirements. However, here are some common parameter settings that you may need to configure:
-
Motor Data: Parameters related to the motor connected to the drive, such as motor rated voltage, rated current, rated frequency, and motor type.
-
Control Mode: Select the control mode of the drive, such as V/Hz control, vector control, or sensorless vector control.
-
Acceleration/Deceleration Times: Set the acceleration and deceleration times to control the speed at which the motor ramps up or down.
-
Maximum/Minimum Frequency: Define the maximum and minimum frequencies at which the motor operates.
-
Current Limiting: Set the maximum current limit to protect the motor from overload conditions.
-
Voltage Boost: Enable or disable voltage boost to compensate for voltage drops during acceleration.
-
Braking: Configure braking settings if using a braking resistor or other braking methods.
-
Fault Handling: Define how the drive responds to various fault conditions, such as whether to trip immediately or attempt a restart.
-
Control Inputs/Outputs: Configure digital and analog inputs and outputs for control and monitoring purposes.
-
Communication: Set up communication parameters if connecting the drive to a PLC or other control system, such as baud rate and communication protocol.
-
Parameter Lock: Optionally, lock certain parameters to prevent unauthorized changes.
-
Display Settings: Adjust settings related to the drive's display, such as brightness and language.
-
Fault Log: View or clear the fault log to monitor and troubleshoot any issues that may arise.
These are just some examples of common parameter settings for an ACS150 drive. The specific parameters and their values will depend on your application and the requirements of your motor control system.
Below list show ABB ACS150 drive parameters:
Macro | ||
9902 | 1 | ABB Standard |
2 | 3-wire | |
3 | Alternate | |
4 | Motor Pot | |
5 | Hand/auto | |
6 | PID Control | |
Motor Data | ||
9905 | …. V | Motor voltage |
9906 | ….A | Motor current |
9907 | ….Hz | Motor Frequency |
9908 | ….rpm | Motor rpm |
9909 | ….KW | Motor power |
Limit | ||
2007 | ….Hz | Min freq. |
2008 | ….HZ | Max. freq. |
ACC/DCC Time | ||
2202 | ….s | Acc time |
2203 | ….s | Dcc time |
Actual Signal | ||
107 | DC Vol. | |
120 | AI | |
160 | DI | |
Start Command | ||
1001 | 8 | Keypad in loc |
4 | 3-wire | |
9 | Start forward start rev. | |
Jog Selection | ||
1010 | ….(DI) | Select DI 1-5 |
1208 | ….Hz | Jog frequency |
1201 | 0 | Constant speed disable |
Constant speed Disable | ||
1201 | 0 | Constant speed disable |
Refrence Selection | ||
1103 | 0 | Keypad |
1 | AI | |
2 | Potentiometer | |
5 | DI3 inc DI4 dec | |
6 | DI3 inc DI4dec (store speed) | |
Min/Max Ref | ||
1104 | ….Hz | Min. ref |
1105 | ….Hz | Max. ref |
Analog Input | ||
1301 | …. % | Min AI |
1302 | …. % | Max AI |
Relay Output | ||
1401 | 1 | Ready |
2 | Run | |
3 | Fault -1 | |
Run Enable | ||
1601 | 0 | Not selected |
Parameter Lock | ||
1602 | 0 | Locked |
1 | Open | |
Pass Code | ||
1603 | ….(358) | |
Local Lock | ||
1606 | 0 | Not selected |
7 | ON | |
Parameter Save | ||
1607 | 1 | Saved |
Max Output Current | ||
2003 | ….A | Max output current |
Brake Chopper Function | ||
2005 | 0 | Disable Overvoltage Function |
1 | Enable | |
2102 | 1 | Coast |
2 | Ramp | |
Start Inhibit | 0 | Off |
1 | on | |
Emergenct Stop | ||
2109 | 0 | 1-5 DI |
Switching Frequency | ||
2606 | 4 Hz | |
8 Hz | ||
12 Hz | ||
16 Hz | ||
External Fault | ||
3003 | 0 | 0-5 DI |
Motor Thermal Protection | ||
3005 | 0 | Not Select |
1 | Fault | |
2 | Alarm | |
Drive Display | ||
3401 | …… | Actual value |