Forum

Share:
Notifications
Clear all

abb acs150 drive parameter settings

1 Posts
1 Users
0 Reactions
1,614 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

The parameter settings for an ABB ACS150 drive can vary depending on your specific application and requirements. However, here are some common parameter settings that you may need to configure:

  1. Motor Data: Parameters related to the motor connected to the drive, such as motor rated voltage, rated current, rated frequency, and motor type.

  2. Control Mode: Select the control mode of the drive, such as V/Hz control, vector control, or sensorless vector control.

  3. Acceleration/Deceleration Times: Set the acceleration and deceleration times to control the speed at which the motor ramps up or down.

  4. Maximum/Minimum Frequency: Define the maximum and minimum frequencies at which the motor operates.

  5. Current Limiting: Set the maximum current limit to protect the motor from overload conditions.

  6. Voltage Boost: Enable or disable voltage boost to compensate for voltage drops during acceleration.

  7. Braking: Configure braking settings if using a braking resistor or other braking methods.

  8. Fault Handling: Define how the drive responds to various fault conditions, such as whether to trip immediately or attempt a restart.

  9. Control Inputs/Outputs: Configure digital and analog inputs and outputs for control and monitoring purposes.

  10. Communication: Set up communication parameters if connecting the drive to a PLC or other control system, such as baud rate and communication protocol.

  11. Parameter Lock: Optionally, lock certain parameters to prevent unauthorized changes.

  12. Display Settings: Adjust settings related to the drive's display, such as brightness and language.

  13. Fault Log: View or clear the fault log to monitor and troubleshoot any issues that may arise.

These are just some examples of common parameter settings for an ACS150 drive. The specific parameters and their values will depend on your application and the requirements of your motor control system.

Below list show ABB ACS150 drive parameters:

Macro    
     
9902 1 ABB Standard
  2 3-wire
  3 Alternate
  4 Motor Pot
  5 Hand/auto
  6 PID Control
     
Motor Data    
     
9905 …. V Motor voltage
9906 ….A Motor current
9907 ….Hz Motor Frequency
9908 ….rpm Motor rpm
9909 ….KW Motor power
     
Limit    
     
2007 ….Hz Min freq.
2008 ….HZ Max. freq.
     
ACC/DCC Time    
     
2202 ….s Acc time
2203 ….s Dcc time
     
Actual Signal    
     
107 DC Vol.  
120 AI  
160 DI  
     
Start Command    
     
1001 8 Keypad in loc
  4 3-wire
  9 Start forward start rev.
     
Jog Selection    
     
1010 ….(DI) Select DI 1-5
1208 ….Hz Jog frequency
     
1201 0 Constant speed disable
     
Constant speed Disable    
     
1201 0 Constant speed disable
     
Refrence Selection    
     
1103 0 Keypad
  1 AI
  2 Potentiometer
  5 DI3 inc DI4 dec
  6 DI3 inc DI4dec (store speed)
     
     
Min/Max Ref    
     
1104 ….Hz Min. ref
1105 ….Hz Max. ref
     
Analog Input    
     
1301 …. % Min AI
1302 …. % Max AI
     
Relay Output    
     
1401 1 Ready
  2 Run
  3 Fault -1
     
Run Enable    
     
1601 0 Not selected
     
Parameter Lock    
     
1602 0 Locked
  1 Open
     
Pass Code    
     
1603 ….(358)  
     
Local Lock    
     
1606 0 Not selected
  7 ON
     
Parameter Save    
     
1607 1 Saved
     
Max Output Current    
     
2003 ….A Max output current
     
Brake Chopper Function    
     
2005 0 Disable Overvoltage Function
  1 Enable
     
2102 1 Coast
  2 Ramp
     
Start Inhibit 0 Off
  1 on
     
Emergenct Stop    
2109 0 1-5 DI
     
Switching Frequency    
     
2606 4 Hz  
  8 Hz  
  12 Hz  
  16 Hz  
     
External Fault    
     
3003 0 0-5 DI
     
Motor Thermal Protection    
     
3005 0 Not Select
  1 Fault
  2 Alarm
     
Drive Display    
     
3401 …… Actual value