Cause : Output phase loss - comes when motor circuit fault due to missing motor connection due to any of the three phases not connected.
- In scalar control mode, the drive detects fault only when the output frequency is above 10% of the motor nominal frequency.
- This fault can be disable - programmable fault: 31.19 Motor phase loss Connect motor cable.
- If the drive is in scalar mode and nominal current of the motor is less than 1/6 of the nominal output current of the drive, set parameter 31.19 Motor phase loss to No action.