64A6 fault in ABB ACS180 drive

1 Posts
1 Users
0 Reactions
333 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Adaptive program file incompatible or corrupted - comes when adaptive program has faulted due to program corrupted or block non-existent. Check aux code for more information :

  1. 000A - Program corrupted or block non-existent : Restore the template program or download the program to the drive.
  2. 000C - Required block input missing : Check the inputs of the block.
  3. 000E - Program corrupted or block non-existent : Restore the template program or download the program to the drive.
  4. 0011 - Program too large : Remove blocks until the error stops.
  5. 0012 - Program is empty. Correct the program and download it to the drive.
  6. 001C - A non-existing parameter or block is used in the parameter : Edit the program to correct the parameter reference, or use an existing block.
  7. 001E - Output to parameter failed because the parameter was write-protected : Check the parameter reference in the program. Check for other sources affecting the target parameter.
  8. 0023 - Program file incompatible with current firmware version : Adapt the program to current block library and firmware version
  9. 0024 - Program file incompatible with current firmware version: Adapt the program to current block library and firmware version.

 