ABB ACS180 Drive
2
Posts
1
Users
0
Reactions
379
Views
Jul 13, 2023 10:33 am
A2B3 Warning in ABB ACS180 drive comes when drive has detected load unbalance typically due to earth fault in motor or motor cable.
1 Reply
Jul 13, 2023 10:34 am
Cause : Earth leakage - comes when drive has detected load unbalance typically due to earth fault in motor or motor cable. Follow these steps to correct fault :
1. Check there are no power factor correction capacitors or surge absorbers in motor cable.
2. Check for an earth fault in motor or motor cables by measuring the insulation resistances of motor and motor cable.