A3A1 warning in ABB ACS180 drive

2 Posts
1 Users
0 Reactions
353 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

A3A1 warning in ABB ACS180 drive comes when intermediate circuit DC voltage too high when the drive is stopped.

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : DC link overvoltage - comes when intermediate circuit DC voltage too high when the drive is stopped. Check following to correct fault :

  1. Check the supply voltage setting (parameter 95.01 Supply voltage).
  2. Note that the wrong setting of the parameter may cause the motor to rush uncontrollably, or may overload the brake chopper or resistor.
  3. Check the supply voltage.