Cause : AI parametrization - comes when the current/voltage hardware setting of an analog input does not correspond to parameter settings.
- Check the event log for an auxiliary code.
- The code identifies the analog input whose settings are in conflict.
- Adjust parameter 12.15/ 12.25.
Note: Control board reboot (either by cycling the power or through parameter 96.08 Control board boot) is required to validate any changes in the hardware settings.