ABB ACS180 Drive
1
Posts
1
Users
0
Reactions
273
Views
Jul 13, 2023 12:52 pm
Cause : ULC configuration - comes when user load curve configuration error due to speed points inconsistent or Frequency points inconsistent.
Check the auxiliary code. See actions for each code below :
- 0000 - Speed points inconsistent : Check that each speed point (parameters 37.11… 37.15) has a higher value than the previous point.
- 0001 - Frequency points inconsistent : Check that each frequency point ( 37.16… 37.20) has a higher value than the previous point.
- 0002 - Underload point above overload point : Check that each overload point ( 37.31… 37.35) has a higher value than the corresponding underload point ( 37.21… 37.25).
- 0003 - Overload point below underload point : Check that each overload point ( 37.31… 37.35) has a higher value than the corresponding underload point ( 37.21… 37.25).