Cause : BC IGBT excess temperature comes when brake chopper IGBT temperature has exceeded internal warning limit.
- Let chopper cool down.
- Check for excessive ambient temperature.
- Check for cooling fan failure.
- Check for obstructions in the air flow.
- Check the dimensioning and cooling of the cabinet.
- Check resistor overload protection function settings (parameters 43.06… 43.10).
- Check minimum allowed resistor value for the chopper being used.
- Check that braking cycle meets allowed limits.