Hello people!
I'm a novice user of ABB drives (and all drives) so sorry if my questions are stupid or easy. I need help with the default macro connection. I need to know how to display the fault in the drive and transmit it to the signal light or PLC. In the default macro connections example, relay with connections 5=NC, 6=COM and 7=NO is marked to show if no fault occurs. Some of my colleagues say, it can be different, you can reprogram it as you want etc...
I don't need all these complications, I just want to use the default state so my question is:
With no fault, will 5 and 6 stay closed and with a drive error, will 6 and 7 close?
Thank you very much!
jmns
Set parameter 10.24 - 14 (Fault)
Thanks for help!
Some of my coleagues helped over phone when we were on site. We set parameter 10.21=0001; 11.02=0001; 11.06=7 and its works! Here is the wiring diagram attached.