A5013 alarm in ABB ACS310
How can resolve problem A5013 alarm in ABB ACS310 ?
Cause : Panel control is disabled because start inhibit is active.
Start from panel is not possible.
Reset emergency stop command or remove 3-wire stop command before starting from panel.
See section 3-wire macro and
parameters 1001 EXT1 COMMANDS,
1002 EXT2 COMMANDS and
2109 EMERG STOP SEL.
Cause : Button is disabled, because start is inhibited.
set parameter
2108 - 0 (Disables the Start inhibit function.)
1601 - 0 (Disable run enable)
2109 - 0
Sets the Start inhibit function on or off.
If the drive is not actively started and running, the Start inhibit function ignores a pending start command in any of the following situations and a new start command is required.
A fault is reset.
Run Enable (parameter 1601) activates while start command is active.
Mode changes from local to remote.
Control switches from EXT1 to EXT2.
Control switches from EXT2 to EXT1