F0002 DC OVERVOLT Fault in ABB ACS310 Drive

2 Posts
1 Users
0 Reactions
903 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0002 DC OVERVOLT Fault in ABB ACS310 Drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Intermediate circuit DC voltage is excessive. Check for and correct:
Static or transient overvoltages in the input power supply.
Insufficient deceleration time (parameters 2203 DECELER TIME 1 and
2206 DECELER TIME 2).
Undersized brake chopper (if present).
Verify that overvoltage controller is ON (using parameter 2005).