Cause : DC OVERVOLTAGE comes when the voltage level in the drive's internal DC link circuit has exceeded its safe operating limit.
The F0002 code you're encountering on your ABB ACS310 drive indicates a DC overvoltage fault. This means the voltage level in the drive's internal DC link circuit has risen above its safe operating limit.
- Check that overvoltage controller is on (parameter 2005 OVERVOLT CTRL).
- Check input power line for static or transient overvoltage.
- Check deceleration time (2203, 2206).