F0022 fault in ABB ACS310 drive

1 Posts
1 Users
0 Reactions
393 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : SUPPLY PHASE comes when intermediate circuit DC voltage is oscillating due to missing input power line phase or blown fuse.

The F0022 code in your ABB ACS310 drive indicates a supply phase fault. This means the drive is detecting an issue with the AC power supply feeding the unit.

  1. Trip occurs when DC voltage ripple exceeds 14% of nominal DC voltage.
  2. Check input power line fuses.
  3. Check for input power supply imbalance.
  4. Check fault function parameters.