How can resolve problem F0035 OUTP WIRING Fault in ABB ACS310 Drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Incorrect input power and motor cable connection (i.e., input power cable is connected to drive motor connection).

The fault can be erroneously declared if the drive is faulty or the input power is a delta grounded system and the motor cable capacitance is large.

This fault can be disabled by using parameter 3023 WIRING FAULT.

Check input power connections.

Check grounding.