F1001 fault in ABB ACS310 drive

1 Posts
1 Users
0 Reactions
15 Views
Posts: 16326
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : PAR PFC REF NEG comes when an issue with the PFC parameters. This fault can occur if the drive's configuration settings related to PFC are not correctly set or are incompatible with the system requirements.

  • Check parameter group 81 PFC CONTROL settings.
  • Check thatfollowing applies:
    • 2007 MINIMUM FREQ > 0 when 8123 is ACTIVE or SPFC ACTIVE.