ABB ACS310 Drive
2
Posts
1
Users
0
Reactions
681
Views
Dec 18, 2021 11:21 am
How can resolve problem F1012 PAR PFC IO 1 Fault in ABB ACS310 Drive ?
1 Reply
Dec 18, 2021 11:22 am
Cause : I/O configuration for PFC not complete.
Check parameter settings. Following must apply:
• There are enough relays
parameterized for PFC.
• No conflict exists between
parameter group 14 RELAY OUTPUTS,
parameter 8117 NR OF AUX MOT and
parameter 8118 AUTOCHNG INTERV.