Forum

Share:
Notifications
Clear all

F1017 fault in ABB ACS310 drive

1 Posts
1 Users
0 Reactions
236 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : PAR SETUP 1 comes when it is not allowed to use frequency input signal and frequency output signal simultaneously.

Disable frequency output or frequency input:

• change transistor output to digital mode (value of parameter 1804 TO MODE = DIGITAL), or

• change frequency input selection to other value in parameter groups 11 REFERENCE SELECT, 40 PROCESS PID SET 1, 4

Share: