How can resolve problem A5001 alarm in ABB ACS355 ?
3 Replies
Dec 16, 2021 9:42 am
Cause : Drive is not responding.
1. Check panel connection.
Nov 09, 2023 2:56 am
For A5001 (Drive not responding) issue, it was found that there is no DC3.3V at the connector X3 at WINT1011C power board.
IC A843 (DC DC buck converter P/N: ADP2301AUJZ) was found faulty.
After replacement, no more A5001.