A5013 alarm in ABB ACS355

3 Posts
1 Users
0 Likes
1,632 Views
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

How can resolve problem A5013 alarm in ABB ACS355 ?

2 Replies
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Panel control is disabled because start inhibit is active.

Start from panel is not possible.

Reset emergency stop command or remove 3-wire stop command before starting from panel.

See section 3-wire macro and

parameters 1001 EXT1 COMMANDS,

1002 EXT2 COMMANDS and

2109 EMERG STOP SEL.

Reply
Posts: 14785
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Button is disabled, because start is inhibited.

set parameter

2108 - 0 (Disables the Start inhibit function.)

1601 - 0 (Disable run enable)

2109 - 0

Sets the Start inhibit function on or off.

If the drive is not actively started and running, the Start inhibit function ignores a pending start command in any of the following situations and a new start command is required.

• A fault is reset.
• Run Enable (parameter 1601) activates while start command is active.
• Mode changes from local to remote.
• Control switches from EXT1 to EXT2.
• Control switches from EXT2 to EXT1

Reply