How can resolve problem F0010 PANEL LOSS Fault in ABB ACS355 Drive ?
1 Reply
Dec 16, 2021 11:37 am
Panel communication is lost and either:
• Drive is in local control mode (the control panel displays LOC), or
• Drive is in remote control mode (REM) and is parameterized to accept
start/stop, direction or reference from the control panel.
To correct check:
• Communication lines and connections.
• Parameter 3002 PANEL COMM ERR.
• Parameters in Group 10: START/STOP/DIR and Group 11:
REFERENCE SELECT (if drive operation is REM)