Forum

Share:
Notifications
Clear all

F0010 PANEL LOSS Fault in ABB ACS355 Drive

2 Posts
1 Users
0 Reactions
4,661 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F0010 PANEL LOSS Fault in ABB ACS355 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Panel communication is lost and either:
Drive is in local control mode (the control panel displays LOC), or
Drive is in remote control mode (REM) and is parameterized to accept
start/stop, direction or reference from the control panel.
To correct check:
Communication lines and connections.
Parameter 3002 PANEL COMM ERR.
Parameters in Group 10: START/STOP/DIR and Group 11:
REFERENCE SELECT (if drive operation is REM)

Reply
Share: