ABB ACS355 Drive
2
Posts
1
Users
0
Reactions
1,208
Views
Dec 16, 2021 12:24 pm
How can resolve problem F1009 PAR PCU 1 Fault in ABB ACS355 Drive ?
1 Reply
Dec 16, 2021 12:24 pm
Parameter values for power control are inconsistent: Improper motor
nominal frequency or speed. Check for both of the following:
• 1 < (60 · 9907 MOTOR NOM FREQ / 9908 MOTOR NOM SPEED < 16
• 0.8 < 9908 MOTOR NOM SPEED /
(120 · 9907 MOTOR NOM FREQ / Motor Poles) < 0.992