Forum

Share:
Notifications
Clear all

F1009 PAR PCU 1 Fault in ABB ACS355 Drive

2 Posts
1 Users
0 Reactions
1,208 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F1009 PAR PCU 1 Fault in ABB ACS355 Drive ?

1 Reply
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Parameter values for power control are inconsistent: Improper motor
nominal frequency or speed. Check for both of the following:
1 < (60 · 9907 MOTOR NOM FREQ / 9908 MOTOR NOM SPEED < 16
0.8 < 9908 MOTOR NOM SPEED /
(120 · 9907 MOTOR NOM FREQ / Motor Poles) < 0.992

Reply
Share: