F1017 PAR SETUP 1 Fault in ABB ACS355 Drive

2 Posts
1 Users
0 Reactions
910 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem F1017 PAR SETUP 1 Fault in ABB ACS355 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Only two of the following can be used simultaneously: MTAC- 01 pulse encoder interface module, frequency input signal or frequency output signal.

Disable frequency output, frequency input or encoder:
change transistor output to digital
mode (value of parameter 1804 TO
MODE = 0 [DIGITAL]), or
change frequency input selection to
other value in parameter groups
11 REFERENCE SELECT,
40 PROCESS PID SET 1,
41 PROCESS PID SET 2 and
42 EXT / TRIM PID, or
disable (parameter 5002ENCODER ENABLE)

and remove MTAC-01 pulse encoder interface module.