Forum
Share:
Notifications
Clear all
2340 Short circuit Fault in ABB ACS380 Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
How can resolve problem 2340 Short circuit Fault in ABB ACS380 Drive ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Short-circuit in motor cable(s) or motor.
1. Check motor and motor cable.
2. Check there are no power factor correction capacitors or surge absorbers in motor cable.
3. Remove motor cable then run drive , if fault not coming then drive ok,  run drive with another motor.
Reply