Forum

Share:
Notifications
Clear all

65A1 FBA A parameter conflict Fault in ABB ACS380 Drive

2 Posts
1 Users
0 Reactions
562 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 65A1 FBA A parameter conflict Fault in ABB ACS380 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : The drive does not have a functionality requested by PLC, or requested functionality has not been activated.

1. Check PLC programming.

2. Check settings of parameter groups 50 Fieldbus adapter (FBA) and 51 FBA A settings.

Reply
Share: