How can resolve problem 65A1 FBA A parameter conflict Fault in ABB ACS380 Drive ?
1 Reply
Dec 14, 2021 9:30 am
Cause : The drive does not have a functionality requested by PLC, or requested functionality has not been activated.
1. Check PLC programming.
2. Check settings of parameter groups 50 Fieldbus adapter (FBA) and 51 FBA A settings.