7086 I/O module AI overvoltage Fault in ABB ACS380

2 Posts
1 Users
0 Reactions
1,004 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem 7086 I/O module AI overvoltage Fault in ABB ACS380 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Overvoltage detected in AI. AI is changed to voltage mode from mA mode. AI will return automatically back to mA mode when the AI signal level is within acceptable limits.

1. Check AI signal levels.

2. Remove analog input wire and check fault coming or not.

3. Some time this fault come if you connect wrong connection in analog input 