How can resolve problem 71A2 Mechanical brake closing failed Fault in ABB ACS380 ?
1 Reply
Admin
Topic starter
(@click2electro)
Member
Cause : Mechanical brake control fault. Activated e.g., if brake acknowledgment is not as expected during brake closing.
1. Check mechanical brake connection.
2.Check mechanical brake settings in
parameter group 44 -  Mechanical brake control.
3. Check that the acknowledgment signal matches the actual status of the brake.