How can resolve problem 80A0 AI supervision Fault in ABB ACS380 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : An analog signal is outside the limits specified for the analog input.

1. Programmable fault:

12.03 AI supervision function.

2. Check signal level at the analog input.
3. Check the auxiliary code.
4. Check the wiring connected to the input.
5. Check the minimum and maximum limits of the input in parameter group 12 Standard AI.

0001  AI1LessMIN

0002  AI1GreaterMAX

0003  AI2LessMIN

0004  AI2GreaterMAX