How can resolve problem 80A0 AI supervision Fault in ABB ACS380 Drive ?
1 Reply
Cause : An analog signal is outside the limits specified for the analog input.
1. Programmable fault:
12.03 AI supervision function.
2. Check signal level at the analog input.
3. Check the auxiliary code.
4. Check the wiring connected to the input.
5. Check the minimum and maximum limits of the input in parameter group 12 Standard AI.
0001Â AI1LessMIN
0002Â AI1GreaterMAX
0003Â AI2LessMIN
0004Â AI2GreaterMAX