A686 Checksum mismatch warning in ABB ACS380

2 Posts
1 Users
0 Reactions
367 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A686 Checksum mismatch warning in ABB ACS380 ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : The calculated parameter checksum does not match any enabled reference checksum.

Programmable warning:
96.54 Checksum action

1. Check that all necessary approved (reference) checksums (96.71...96.72) are enabled in 96.55 Checksum control word.

2. Check the parameter configuration.

Using 96.55 Checksum control word, enable a checksum parameter and copy the actual checksum into that parameter.