How can resolve problem A6E6 ULC configuration warning in ABB ACS380 Drive ?
Cause : User load curve configuration error.
1. Check the auxiliary code (format XXXX ZZZZ). “ZZZZ” indicates the problem
(see actions for each code below).
0000 Speed points inconsistent. Check that each speed point (parameters 37.11…37.15) has a higher value than the previous point.
0001 Frequency points inconsistent Check that each frequency point (37.20…37.16) has a higher value than the previous point.
0002 Underload point above overload point. Check that each overload point (37.31…37.35) has a higher value than the corresponding underload
0003 Overload point below underload point point (37.21…37.25).