A7EE Panel loss warning in ABB ACS380 Drive

2 Posts
1 Users
0 Reactions
509 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A7EE Panel loss warning in ABB ACS380 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Control panel or PC tool selected as active control location for drive has ceased communicating.

1. Programmable warning:

49.05 - Communication loss action

2. Check PC tool or control panel connection.

3. Check control panel connector.

4. Replace control panel in mounting platform.