Forum

Share:
Notifications
Clear all

AFEC External power signal missing warning in ABB ACS380 Drive

2 Posts
1 Users
0 Reactions
1,608 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem AFEC External power signal missing warning in ABB ACS380 Drive ?

1 Reply
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : 95.04 - Control board supply is set to External 24V but no voltage is connected to the control unit.

Check the external 24 V DC power supply to the control unit, or change the setting of

parameter 95.04.

Reply
Share: