D100 Torque prove Fault in ABB ACS380 Drive

2 Posts
1 Users
0 Reactions
3,125 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem D100 Torque prove Fault in ABB ACS380 Drive ?

1 Reply
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Drive was not able to provide sufficient torque during Torque proving.The pre-magnetizing time mode is wrong or too short.

Check the motor and motor cables.
Check that the parameter settings are as
follows:
21.01 Vector start mode = Const time
21.02 Magnetization time = Setting is
not fixed. Enter an appropriate value.