ABB ACS550 Drive
2
Posts
1
Users
0
Reactions
1,818
Views
Dec 15, 2021 11:42 am
How can resolve problem A2001 OVERCURRENT Alarm in ABB ACS550 Drive ?
1 Reply
Dec 15, 2021 11:42 am
Current limiting controller is active. Check for and correct:
• Excessive motor load.
• Insufficient acceleration time (parameters 2202 ACCELER TIME 1 and
2205 ACCELER TIME 2).
• Faulty motor, motor cables or connections.