A2002 OVERVOLTAGE Alarm in ABB ACS550 Drive

4 Posts
2 Users
0 Reactions
3,206 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

How can resolve problem A2002 OVERVOLTAGE Alarm in ABB ACS550 Drive ?

3 Replies
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Overvoltage controller is active. Check for and correct:
Static or transient overvoltages in the input power supply.
Insufficient deceleration time (parameters 2203 DECELER TIME 1 and
2206 DECELER TIME 2).

Reply
1 Reply
(@sheldon44)
Joined: 2 years ago

New Member
Posts: 1

@click2electro I’m having this problem any suggestions 

 

Reply
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Check input supply voltage.

If input supply is ok then check DC voltage in parameter group 1

Parameter 0107 - .... DC voltage.

If all are ok then increase  de-acceleration time 

Parameter 2203 - ......

Please also share above reading and what is condition of fault means fault comes when you stop drive or comming continuously.

Reply